Post subject: 12 Pulse VFD Short-Circuit and Arc Flash Calculations
Posted: Thu May 12, 2022 6:22 am
Joined: Thu Jun 09, 2016 6:17 pm Posts: 8
Hi,
When modeling a 12-Pulse VFD that is fed from multiple transformers or a single multi-winding transformer, is it common to only utilize the fault current from one of the two transformers/windings? If the VFD input sources are within the same enclosure, should a scenario be considered where a fault could propagate from one source to the other and both sources of fault current should be considered?