 Post subject: 12 Pulse VFD Short-Circuit and Arc Flash Calculations
PostPosted: Thu May 12, 2022 6:22 am 

Joined: Thu Jun 09, 2016 6:17 pm
Posts: 11
Hi,

When modeling a 12-Pulse VFD that is fed from multiple transformers or a single multi-winding transformer, is it common to only utilize the fault current from one of the two transformers/windings? If the VFD input sources are within the same enclosure, should a scenario be considered where a fault could propagate from one source to the other and both sources of fault current should be considered?

Thanks for the input.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: 12 Pulse VFD Short-Circuit and Arc Flash Calculations
PostPosted: Tue Nov 01, 2022 4:01 am 

Joined: Thu Jun 09, 2016 6:17 pm
Posts: 11
Hi,

Anyone have any input or guidance regarding this?

Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: 12 Pulse VFD Short-Circuit and Arc Flash Calculations
PostPosted: Wed Nov 02, 2022 1:37 pm 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 612
Same enclosure and no barriers? Yes, I would consider a fault involving both sources.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883