12 Pulse VFD Short-Circuit and Arc Flash Calculations
https://brainfiller.com/arcflashforum/viewtopic.php?f=23&t=5575
Page 1 of 1

Author:  makoester1 [ Thu May 12, 2022 6:22 am ]
Post subject:  12 Pulse VFD Short-Circuit and Arc Flash Calculations

Hi,

When modeling a 12-Pulse VFD that is fed from multiple transformers or a single multi-winding transformer, is it common to only utilize the fault current from one of the two transformers/windings? If the VFD input sources are within the same enclosure, should a scenario be considered where a fault could propagate from one source to the other and both sources of fault current should be considered?

Thanks for the input.

Author:  makoester1 [ Tue Nov 01, 2022 4:01 am ]
Post subject:  Re: 12 Pulse VFD Short-Circuit and Arc Flash Calculations

Hi,

Anyone have any input or guidance regarding this?

Thanks

Author:  stevenal [ Wed Nov 02, 2022 1:37 pm ]
Post subject:  Re: 12 Pulse VFD Short-Circuit and Arc Flash Calculations

Same enclosure and no barriers? Yes, I would consider a fault involving both sources.