| Author: | Tesla13 [ Mon May 29, 2023 11:56 am ] |
| Post subject: | Grid short circuit data |
Hi all, I would like to have your view regarding external grid short circuit scenarios in Arc Flash calculations. I have some doubts about how this issue should be addressed. What should I do if there is no info about the available short circuit power in the grid? As far as I understand, considering only hypothetical maximum and minimum short circuit scenarios for calculation I may not be achieving the “Worst Case” incident energy scenario. The reason is that there may be some intermediate Scc scenarios in which the combination of FCT + Icc may lead to a higher Incident Energy. So the correct approach may be doing a sweep with different values. There is also some scientific literature with conclusions pointing in the same direction. Similar happens when the utility gives you the data: what about short circuit intermediate scenarios? How do you see it? Thanks for your support. Regards, |
|
| Author: | Tesla13 [ Fri Jun 30, 2023 12:56 am ] |
| Post subject: | Re: Grid short circuit data |
Up! |
|
| Author: | mpparent [ Fri Jun 30, 2023 6:50 am ] |
| Post subject: | Re: Grid short circuit data |
I think Jim has an article somewhere about this topic. Mike |
|