Had a customer comment on placing lump motor loads on MCC's for modeling. We do this form small motors less than 50 HP but he had a site where another firm had huge loads added which made the MCC bus Dangerous and higher than the line side of the main breaker. How do others address this? Maybe put them in but turn them off for the arc flash calculations? Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Fault calculations.
PostPosted: Fri Aug 18, 2023 4:56 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
If it's a new design I generally model everything off each MCC no matter the size as the design progresses and I'm developing the single line. Even though there is an "exception" for motors smaller than 50 hp for arc flash calcs, I don't think there is such a thing for short circuit calcs, but I could be wrong.

If I'm doing an arc flash study on an existing installation I discuss what all will be included and what won't with the client and price accordingly.

I try not to "lump" motors if I can help it.

Here's the SKM check box Mike is referring to:


Attachment:
50 hp exclusion.jpg
50 hp exclusion.jpg [ 94.5 KiB | Viewed 4902 times ]

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883