 Post subject: Modeling a Transformer as Utility
PostPosted: Tue Jul 30, 2024 9:34 am 

Joined: Wed Jul 24, 2024 1:07 pm
Posts: 11
Location: Texas
If I'm taping from the secondary of a 480V transformer (750KVA, 12.47kv-480V) Z=5.25%) to power my low voltage MCC, do I still need the information from the utility which is powering that transformer? Or should I just model my transformer as the "utility" ?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling a Transformer as Utility
PostPosted: Tue Jul 30, 2024 12:27 pm 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 488
Location: Indiana
Depends on what you're trying to determine. If you're just looking to calculate maximum bolted fault current then assume an infinite bus primary and have all your motor loads accounted for.

If you're doing an arc flash study s well, I'd recommend obtaining the utility company data and modeling it as accurately as possible.

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling a Transformer as Utility
PostPosted: Tue Jul 30, 2024 1:36 pm 

Joined: Wed Jul 24, 2024 1:07 pm
Posts: 11
Location: Texas
Thank you bbaumer.
Now when I asked for the system equivalent at the point of interconnection, or the short circuit, someone asked: "well the point of interconnection for us is the disconnect switch at the pole from the transformer. Why don't you use the ratings for that disconnect?"
And I don't know the answer to that. Could you, or someone, please explain?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling a Transformer as Utility
PostPosted: Tue Jul 30, 2024 2:22 pm 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 488
Location: Indiana
I don't understand whoever said that and I don't think they do either.

Are you / they talking about the primary side cutouts or is there an exterior, 480V service disconnect?

Different utilities have different rules or requirements for their customers as far as where their stuff ends and the customers begins.

Your maximum available at the transformer secondary is going to be something like 750000/480/1.732/0.0525 = 17, 184 amps plus motor contribution. I would probably spec a 65kA MCC if it were me but you could go lower.

Again, if you're doing an arc flash study, it's best to obtain the actual available fault current data from the utility at whatever point on the system they determine and go from there.

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling a Transformer as Utility
PostPosted: Wed Jul 31, 2024 8:25 am 

Joined: Wed Jul 24, 2024 1:07 pm
Posts: 11
Location: Texas
bbrent thak you for your reply.

I'm attaching a drawing to better explain myself:

1)Do I ONLY need the short circuit from the 480VAC EXISTING POWER DISTRIBUTION PANEL? or do I need the info from where that POWER DISTRIBUTION panel is connected to?

2) The question asked was: since we are connecting the panel to a delta delta transformer and that to a 100A fused disconnect at that to another fused disconnect, he is asking if our point of connection is the first fused disconnect instead of the 480V EXISTING POWER DISTRIBUTION PANEL and thus we only need the info of that first fused disconnect instead of the 480V EXISTING POWER DISTRIBUTION PANEL


Attachments:
One Line question.pdf [27.93 KiB]
Downloaded 820 times
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling a Transformer as Utility
PostPosted: Wed Jul 31, 2024 1:03 pm 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 488
Location: Indiana
1. If you can get the available fault current at that distribution panel that will be fine an you can model that as the utility, you still need the feeder size and length from that distribution panel to the first disconnect though.

2. Not sure I understand question 2 but if so, you need the fault current at the upstream distribution panel and feeder data as described in 1. above OR if they can tell you the available fault current at the first fused disconnect switch instead that would work too as your "UTILITY".

Attachment:
AVAILABLE FAULT CURRENT.jpg
AVAILABLE FAULT CURRENT.jpg [ 59.18 KiB | Viewed 9639 times ]

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling a Transformer as Utility
PostPosted: Wed Jul 31, 2024 1:08 pm 

Joined: Wed Jul 24, 2024 1:07 pm
Posts: 11
Location: Texas
bbaumer Everything has been clearly explained and hence clearly comprehended.

THANK YOU!


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling a Transformer as Utility
PostPosted: Wed Jul 31, 2024 1:14 pm 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 488
Location: Indiana
Glad I could help.

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 8 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883