 Post subject: Modeling an extruder in skm
PostPosted: Mon Nov 04, 2024 2:34 pm 

Joined: Wed Jun 12, 2024 5:19 am
Posts: 33
Hello,
My field tech gave me a drawing of an extruder control panel and I don't know how to model it in SKM.
Two breakers are from a panel and then they go into the control panel. inside the control panel is another breaker that feeds the drive. How do I show that in SKM?


Attachments:
File comment: This is how I have it modeled.
SKM Model for Extruder 2.jpg
SKM Model for Extruder 2.jpg [ 88.28 KiB | Viewed 18412 times ]
File comment: The Field Tech's Drawings
Extruder 2- CP.jpg
Extruder 2- CP.jpg [ 55.38 KiB | Viewed 18412 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling an extruder in skm
PostPosted: Mon Nov 11, 2024 1:13 pm 
Sparks Level

Joined: Fri Sep 28, 2018 7:32 am
Posts: 57
Location: Sioux Falls, SD
What you have will work. Effectively, you must analyze separate points representing the different inputs into the cabinet. You will then apply the arc flash label associated with the worst case hazard. Note that the worst case arc flash hazard is likely from the lower voltage feed but the maximum voltage exposure will be from your separate 480V circuit.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883