 Post subject: Low Impedance Cable
PostPosted: Fri Nov 08, 2024 4:18 pm 

Joined: Wed Jun 12, 2024 5:19 am
Posts: 35
Hello,
Does anyone know how to model this Low Impedance Cable? I am trying to show the line side and the load side of a Switchboard on SKM. I found this page.
https://www.skm.com/SKM_Arc_Flash_Line_ ... 0Side.html


Attachments:
Low Impedance Cable.jpg
Low Impedance Cable.jpg [ 19.26 KiB | Viewed 20596 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Low Impedance Cable
PostPosted: Fri Nov 08, 2024 4:49 pm 

Joined: Tue Mar 20, 2018 11:55 am
Posts: 3
I would select a large cable (e.g. 500 kcmil or larger), make cable length minimum (0.1 feet I think is SKMs minimum length), and add multiple cables in parallel. I believe the reporting option 'Report line side and load side' may provide the results that you are looking for without the need for this cable. As far as making the cable symbol different than other cable symbols, I haven't investigated how to do that - I just label the cable as a DUMMY_CABLE and move on.