| Author: | mpparent [ Tue Dec 17, 2024 6:23 am ] |
| Post subject: | Re: My Line side is the same Incident energy as my Load side |
I'll take a stab: unless you have a remote main, the main OCPD in the electrical equipment is not used and the upstream OCPD is used. Since the AF plasma expands at the rate of dynamite, it can be useless in open switchgear and you end up with a 3 phase fault on both the line and load. Mike |
|