JBD wrote:
A bank of single transformers is consider as a single three phase transformer, if they are all the same size and impedance.
(3) 75kVA units equals (1) 225kVA unit.
^^^^ This ^^^^
Also note that the %Z does NOT triple and will likely be much lower than a typical 3 phase transformer. Those single phase cans are more like 1.2%, not 4 or 5% or so. This means your secondary available fault current will be higher than it is with a typical 3 phase unit.