 Post subject: Series Rating a Panelboard.
PostPosted: Tue Aug 05, 2025 5:02 am 

Joined: Wed Jun 12, 2024 5:19 am
Posts: 33
Hello,
If I needed to series-rate a panelboard. Do I enter the rating of the breaker in the Series rating box under the component subview? I know in EasyPower I would select a check mark and it would pass on the device evaluation because it is still showing up as a fail on skm. Am I missing a step?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Series Rating a Panelboard.
PostPosted: Tue Aug 05, 2025 5:54 am 
Sparks Level

Joined: Thu Apr 18, 2019 11:42 am
Posts: 163
In SKM, if you open up a device by double clicking on it, the component editor for that device will appear. You should be on the "protective device" subview, and on that view, there is a "series rating" field. You should be able to fill that in with the appropriate series rating for that device.


Mike


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Series Rating a Panelboard.
PostPosted: Tue Aug 05, 2025 8:08 am 

Joined: Wed Jun 12, 2024 5:19 am
Posts: 33
Yes, but what about the device evaluation? is there a way to show it as passed because it is being series rated?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Series Rating a Panelboard.
PostPosted: Tue Aug 05, 2025 8:46 am 
Sparks Level

Joined: Thu Apr 18, 2019 11:42 am
Posts: 163
I haven't had any issues in the equipment evaluation displaying series rated devices that pass.

Mike


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Series Rating a Panelboard.
PostPosted: Tue Aug 05, 2025 10:42 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 438
Location: Indiana
Mike is correct.

If you enter a series rating in the Component Editor for the device, or bus, and that rating is higher than the X/R adjusted, calculated available fault current, it will pass the Device Evaluation.

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883