Sparks Level

Joined: Fri Mar 28, 2025 2:54 pm
Posts: 78
The subject line might be a little misleading. I keep running into these combos of Westinghouse FB3050 breakers and LFB3070R "current limiters" (BTW, I swear I posted something else about the same thing here but I can't find it--my apologies). see associated image below.

Westinghouse FB breakers from 15-70A were all 14kAIC rated when this combo was being made. The Current Limiter is rated at 200kAIC, but is only designed to be used with those 14kAIC breakers. Does that mean the withstand rating of the breaker should be assessed at 200kAIC?

I can think of legitimate arguments for giving the breaker either rating. The documentation I could find online doesn't explicitly say one way or the other, just that these two devices are designed to work together (in series).


Attachments:
LFB.jpg
LFB.jpg [ 62.6 KiB | Viewed 25981 times ]
IMG_2560.JPG
IMG_2560.JPG [ 4.18 MiB | Viewed 25981 times ]
IMG_2559.JPG
IMG_2559.JPG [ 4.83 MiB | Viewed 25981 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Series-Rated or no?
PostPosted: Mon Oct 13, 2025 1:14 pm 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 619
Location: Wisconsin
Those current limiter modules are intended to provide a 200kA series rating with the specific model breaker, according to my Westinghouse catalog from 1989.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Series-Rated or no?
PostPosted: Wed Oct 15, 2025 7:53 am 
Sparks Level

Joined: Fri Mar 28, 2025 2:54 pm
Posts: 78
JBD wrote:
Those current limiter modules are intended to provide a 200kA series rating with the specific model breaker, according to my Westinghouse catalog from 1989.


THANK YOU!


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Series-Rated or no?
PostPosted: Wed Oct 15, 2025 9:22 am 
Sparks Level

Joined: Fri Mar 28, 2025 2:54 pm
Posts: 78
JBD wrote:
Those current limiter modules are intended to provide a 200kA series rating with the specific model breaker, according to my Westinghouse catalog from 1989.


Would you be willing to post a screenshot of that verbiage and/or reference the catalog information? I'd love to have this info available.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Series-Rated or no?
PostPosted: Thu Oct 16, 2025 12:39 pm 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 619
Location: Wisconsin
NeDCE wrote:
JBD wrote:
Those current limiter modules are intended to provide a 200kA series rating with the specific model breaker, according to my Westinghouse catalog from 1989.


Would you be willing to post a screenshot of that verbiage and/or reference the catalog information? I'd love to have this info available.


These current limiting modules only worked with magnetic only breakers when used with a motor contactor and overload relays.


Attachments:
west.jpg
west.jpg [ 89.56 KiB | Viewed 25711 times ]
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883