It is currently Mon Sep 28, 2026 8:42 am



Post new topic Reply to topic
Author Message
 Post subject: More Utility fun and games
PostPosted: Mon Dec 22, 2025 6:56 pm 
Sparks Level

Joined: Fri Mar 28, 2025 2:54 pm
Posts: 70
Happy Holidays, all!

What do you all do when the Utility's design letter/AFC calculations contain info you know is incorrect? What is our responsibility to the Utility in such cases?

On my most current project, the Utility's stated incoming conductor information is incorrect, both in quantity of conductors and size(8 parallel 750mcm vs 4 parallel 350mcm). I know because I have photo documentation of what's landed on the utility side of the gear. This happens somewhat regularly.

Obviously I want my study to be accurate, so I'm going to model the incoming as the Utility states it and make sure the AFC matches, then see how different the AFC will be with the actual installed conductors.

If, in this case, the AFC was close, would you send a courtesy note to the Utility to let them know their info is incorrect? Do we have a responsibility to do so? If the AFC was significantly different using the installed conductors, does the courtesy become a responsibility?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: More Utility fun and games
PostPosted: Tue Jan 06, 2026 4:15 pm 
Sparks Level

Joined: Fri Mar 28, 2025 2:54 pm
Posts: 70
Nobody? Is this taboo territory?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: More Utility fun and games
PostPosted: Thu Jan 08, 2026 2:32 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 498
Happens once in awhile. Very recently again for me. I'll try to upload a heavily redacted version of the conversation. I just stay after them until they comply or tell me it isn't possible or it is clear it is a lost cause.

Attachment:
Discussion with Utility PDF.pdf [874.07 KiB]
Downloaded 2106 times

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: More Utility fun and games
PostPosted: Thu Jan 08, 2026 7:34 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
That's a difficult one. In a past life, I headed up the short circuit studies group for a large electric utility and we NEVER made mistakes :D (humor)

There are a few option, one is to use an iterative approach which I have discussed here before (and on the brainfiller.com website)
Begin with what you know (incorrect data) and run the study. Note the incident energy and PPE at each location.
Then begin to vary the suspect data. Number per phase, lengths etc. See how that affects the incident energy and PPE.
See if any of the alternative cases change the PPE requirements. Most notably, does the change in fault current, change a protective device's fault clearing time.
After running several alternate cases, this should provide you with a range of validity where the recommended PPE is sufficient.
State these assumptions in the report - i.e. PPE is based on... x,y,z
Not a perfect answer but often, sufficient data is lacking.

Also, yes - notify the electric utility as a CYA move. Just state something like, it was noticed that....

Good luck!


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: More Utility fun and games
PostPosted: Thu Jan 08, 2026 8:24 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 498
Also, as mentioned on here before a few times, I've resorted to sending the POCO a link to this video to get accurate information. It has worked every time so far:

https://www.youtube.com/watch?v=5TPIOAX6Ksk

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: More Utility fun and games
PostPosted: Thu Jan 08, 2026 8:33 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 498
Jim Phillips (brainfiller) wrote:
That's a difficult one. In a past life, I headed up the short circuit studies group for a large electric utility and we NEVER made mistakes :D (humor)

There are a few option, one is to use an iterative approach which I have discussed here before (and on the brainfiller.com website)
Begin with what you know (incorrect data) and run the study. Note the incident energy and PPE at each location.
Then begin to vary the suspect data. Number per phase, lengths etc. See how that affects the incident energy and PPE.
See if any of the alternative cases change the PPE requirements. Most notably, does the change in fault current, change a protective device's fault clearing time.
After running several alternate cases, this should provide you with a range of validity where the recommended PPE is sufficient.
State these assumptions in the report - i.e. PPE is based on... x,y,z
Not a perfect answer but often, sufficient data is lacking.

Also, yes - notify the electric utility as a CYA move. Just state something like, it was noticed that....

Good luck!


Glad to see you participating on here, Jim. I think it's been awhile. At least to my short memory.

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: More Utility fun and games
PostPosted: Thu Jan 08, 2026 1:27 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
Thanks. 2025 was an insane year but nice to be back a bit more! Thank to you and everyone for keeping the conversation moving!


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: More Utility fun and games
PostPosted: Thu Jan 08, 2026 2:22 pm 
Sparks Level

Joined: Fri Mar 28, 2025 2:54 pm
Posts: 70
bbaumer wrote:
Happens once in awhile. Very recently again for me. I'll try to upload a heavily redacted version of the conversation. I just stay after them until they comply or tell me it isn't possible or it is clear it is a lost cause.

Attachment:
Discussion with Utility PDF.pdf

I like how at the end, they give you info without so much as acknowledging any of the previous conversation

Like in the Batman Lego movie, where he hits something with the batarang after missing it 15 times, and yells, "First try!" :D


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: More Utility fun and games
PostPosted: Thu Jan 08, 2026 2:29 pm 
Sparks Level

Joined: Fri Mar 28, 2025 2:54 pm
Posts: 70
Jim Phillips (brainfiller) wrote:
That's a difficult one. In a past life, I headed up the short circuit studies group for a large electric utility and we NEVER made mistakes :D (humor)

There are a few option, one is to use an iterative approach which I have discussed here before (and on the brainfiller.com website)
Begin with what you know (incorrect data) and run the study. Note the incident energy and PPE at each location.
Then begin to vary the suspect data. Number per phase, lengths etc. See how that affects the incident energy and PPE.
See if any of the alternative cases change the PPE requirements. Most notably, does the change in fault current, change a protective device's fault clearing time.
After running several alternate cases, this should provide you with a range of validity where the recommended PPE is sufficient.
State these assumptions in the report - i.e. PPE is based on... x,y,z
Not a perfect answer but often, sufficient data is lacking.

Also, yes - notify the electric utility as a CYA move. Just state something like, it was noticed that....

Good luck!


Thank you! Only tangentially related, but I'm going in circles with a utility over a project I'm doing for the local water district. The district has a turbine in line with the local water line that generates power as it throttles the pressure. This power is stepped up from 480V to 12.4kV from a transformer on the property, and fed back into the grid. It's monitored by a utility-owned meter.

Neither the water district, nor the power utility has any record of owning the transformer, and the Utility has no information on the meter. I'm on my 3rd Utility rep, and as yet. no one has been able to identify this meter that they installed, which has an exclusive number belonging to the Utility, and is in operation.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: More Utility fun and games
PostPosted: Mon Jun 29, 2026 12:23 pm 

Joined: Mon Jun 29, 2026 12:15 pm
Posts: 1
Can anyone else get this video from (bbaumer) to play?

https://youtu.be/5TPIOAX6Ksk?feature=shared

Keeps telling me it's private?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: More Utility fun and games
PostPosted: Wed Jul 01, 2026 9:10 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 498
rhummel@k2mdesign.com wrote:
Can anyone else get this video from (bbaumer) to play?

https://youtu.be/5TPIOAX6Ksk?feature=shared

Keeps telling me it's private?


I took down all my videos until I can figure out how to add an intro to let people know I am retired and also to put some type of disclaimer in the intro to use the information presented in the video at your own risk. I've spent some time on it and it looks like to add an intro I have to edit all the videos individually by adding the intro and re-uploading them all. I made dozens of SKM and power studies related videos so that would be a lot of work I'm not sure I want to do.

I'm down to needing to print one label for a long-time customer as soon as he sends me the info on the panel he added to the system and printing labels for another customer on a study I am done with but am just waiting on owner comments on the final report. After that I will be done and will be selling my SKM license if I find someone interested in it.

I am not taking on any new work.

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: More Utility fun and games
PostPosted: Fri Jul 31, 2026 8:45 am 
Sparks Level

Joined: Fri Mar 28, 2025 2:54 pm
Posts: 70
bbaumer wrote:
rhummel@k2mdesign.com wrote:
Can anyone else get this video from (bbaumer) to play?

https://youtu.be/5TPIOAX6Ksk?feature=shared

Keeps telling me it's private?


I took down all my videos until I can figure out how to add an intro to let people know I am retired and also to put some type of disclaimer in the intro to use the information presented in the video at your own risk. I've spent some time on it and it looks like to add an intro I have to edit all the videos individually by adding the intro and re-uploading them all. I made dozens of SKM and power studies related videos so that would be a lot of work I'm not sure I want to do.

I'm down to needing to print one label for a long-time customer as soon as he sends me the info on the panel he added to the system and printing labels for another customer on a study I am done with but am just waiting on owner comments on the final report. After that I will be done and will be selling my SKM license if I find someone interested in it.

I am not taking on any new work.


Congratulations! I'm incredibly appreciative of your willingness to help out others with your knowledge and expertise. I've learned an incredible amount from your posts and videos thus far.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 12 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883