| Author |
Message |
|
arcflashprimero
|
Post subject: Bolted Pressure Switch Posted: Mon Feb 16, 2026 11:23 am |
|
Joined: Thu Dec 18, 2025 3:21 pm Posts: 11
|
|
any tips on modeling an Eaton bolted pressure switch? switchboard is using a BPS as the main device with ARMS mode. would this be modeled just as a fuse?
|
|
| Top |
|
 |
|
mpparent
|
Post subject: Re: Bolted Pressure Switch Posted: Tue Feb 17, 2026 7:18 am |
|
Joined: Thu Apr 18, 2019 11:42 am Posts: 167
|
|
I think Eatons' offering is actually an arc reduction relay tied to the BPS. In my opinion, you'll model two things:
1. Fuse 2. The arc reduction relay with trip times from the manufacturer. You may have to create your own library file for this one, unless SKM, Easypower, etc. have a model file you can use.
Mike
|
|