| Author: | arcflashprimero [ Mon Feb 16, 2026 11:23 am ] |
| Post subject: | Bolted Pressure Switch |
any tips on modeling an Eaton bolted pressure switch? switchboard is using a BPS as the main device with ARMS mode. would this be modeled just as a fuse? |
|
| Author: | mpparent [ Tue Feb 17, 2026 7:18 am ] |
| Post subject: | Re: Bolted Pressure Switch |
I think Eatons' offering is actually an arc reduction relay tied to the BPS. In my opinion, you'll model two things: 1. Fuse 2. The arc reduction relay with trip times from the manufacturer. You may have to create your own library file for this one, unless SKM, Easypower, etc. have a model file you can use. Mike |
|