 Post subject: Main Circuit Breaker in Panelboard
PostPosted: Wed Sep 23, 2009 1:54 am 

Joined: Wed Sep 23, 2009 1:17 am
Posts: 2
1200 amp 480v, panelboard, main circuit breaker
Fed from utility transformer with only high side fuse
The arc flash rating of the line side of the main is about 80 cal/cm2 based on 2 second clearing time (since the high side fuse will have a clearing time of never).
The panelboard is the type that has seperate covers for the main circuit breaker and feeders, and therefore work could be performed on feeder breakers without removing the cover over the main lugs. It has a servance entrance label.

If the main breaker was turned off, could work be performed on the load side of the breaker, such as adding a feeder breaker?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Sep 23, 2009 6:15 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Jack wrote:
1200 amp 480v, panelboard, main circuit breaker
Fed from utility transformer with only high side fuse
The arc flash rating of the line side of the main is about 80 cal/cm2 based on 2 second clearing time (since the high side fuse will have a clearing time of never).
The panelboard is the type that has seperate covers for the main circuit breaker and feeders, and therefore work could be performed on feeder breakers without removing the cover over the main lugs. It has a servance entrance label.

If the main breaker was turned off, could work be performed on the load side of the breaker, such as adding a feeder breaker?


Depends on the breaker type. Just opening a breaker is not sufficient for isolation purposes oer OSHA. A power circuit breaker needs to be racked out to the disconnect position and locked out for proper isolation.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Sep 23, 2009 2:20 pm 

Joined: Wed Sep 23, 2009 1:17 am
Posts: 2
Main

It's a molded case circuit breaker that is LOTO.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Sep 24, 2009 10:00 pm 
Sparks Level

Joined: Wed Jan 28, 2009 2:19 pm
Posts: 72
Location: Georgia
If the main is locked out and is in a separate compartment, there are no exposed energized conductors. You can install breakers or whatever. However at 80 cal/cm2, the problem comes when operating the 1200 amp main and verifying the absence of voltage.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Sep 24, 2009 10:08 pm 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
JJH wrote:
If the main is locked out and is in a separate compartment, there are no exposed energized conductors. You can install breakers or whatever. However at 80 cal/cm2, the problem comes when operating the 1200 amp main and verifying the absence of voltage.


Operate the breaker remotely.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883