PostPosted: Fri Dec 04, 2009 2:24 pm 

Joined: Thu Apr 02, 2009 5:59 am
Posts: 6
Hi everyone,

I am doing an arc flash study for a generating station that protects the main generator buses through lockout relays (i.e. 50/51/87 etc. element actuates the 86 element which in turn initiates the circuit breaker trip coil). It turns out there is a wide variance of activation times on these lockout relays (from reading on-line specs) and it is not particularly easy to get this data from the client. How does everyone incorporate the 86 element time into their model? I have heard times ranging from 130ms all the way down to 8ms... makes a pretty big difference in HRC.

Thanks in advance for the input.

Tim Ricard


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Dec 18, 2009 11:21 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 532
Electroswitch says .5 cycle.


Top