Before a full, professional study is completed in our facility, I was wondering what type of label to use since we don't have all the information that is needed for a detailed label. We will be using tables until all of our information is gathered. None of our machinery has any types of warning or danger labels. I have found some labels that have "Danger--arc flash and shock hazard. Appropriate PPE required. Refer to NFPA 70E for minimum PPE requirements" Is this enough until we are able to get a study completed?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Aug 12, 2010 1:37 pm 
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
The NEC (which I believe is law in every state) requires it.
For Canadians, the CEC (law in every province) has a very similar requirement.

So your equipment should already have those basic warning labels.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Aug 16, 2010 5:39 am 

Joined: Mon Jul 19, 2010 11:18 am
Posts: 7
Location: Tennessee
There is hardley any of our machines that have any warning labels on them. Every now and then, you may see a high voltage sticker. How has anyone else who will have a study done, (in the future) labeled their machines until it is completed? You don't know what the PPE requirements are, unless you use the worse case senerio from the charts?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Aug 16, 2010 12:53 pm 

Joined: Wed Jan 20, 2010 4:08 am
Posts: 14
http://www.bradyid.com/bradyid/pdpv/101520.html


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Oct 27, 2010 12:18 pm 
Sparks Level
User avatar

Joined: Tue Oct 26, 2010 5:00 pm
Posts: 196
Location: Maple Valley, WA.
Putting a label on the equipment warning of the AF hazard does not relieve you or your company of the responsibility to perform an Arc Flash Hazard analysis. Attaching labels without the Hazard Category or Cals/cm2 serves no useful or legal value. I would recommend instructing the staff on how to use the NFPA 70E task tables until you get an analysis performed and labels attached. This is better than nothing. Also, I recommend that your staff wear HRC 2 clothing for everyday work since 90% of the equipment will be HRC 2 or less.

_________________
Robert Fuhr, P.E.; P.Eng.
PowerStudies


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883