PostPosted: Thu May 05, 2011 6:06 am 

Joined: Wed Nov 10, 2010 5:26 pm
Posts: 5
I haven't seen much discussion of this on this forum but I've run into this issue several times. Since the requirement to field-mark certain electrical equipment to warn of potential arc flash hazards was first introduced in Section 110-16 of the 2002 National Electrical Code, and Arc flash markings were first mentioned in the 2004 edition of NFPA 70E, some people interpret this as equipment installed before 2002 must be labeled only if any modifications or upgrades are done to the equipment.

Has anyone run across any good articles which discuss this?

Does anyone use this as justification to not label equipment installed prior to 2002 that hasn't been modified?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu May 05, 2011 7:55 am 
Sparks Level

Joined: Mon Mar 29, 2010 11:52 am
Posts: 110
Location: Yankton SD/ Lead SD
The NEC is a forward looking document, and as such, does not require retroactive compliance.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu May 05, 2011 8:07 am 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 544
Location: Wisconsin
cbauer wrote:
The NEC is a forward looking document, and as such, does not require retroactive compliance.


Arc Flash labeling, to allow selection of proper PPE, is required by NFPA70E which does require 'retroactive' compliance.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883