 Post subject: NFPA 130.3 Arc Flash Hazard Analysis-Exception No. 1
PostPosted: Mon Feb 24, 2014 5:02 pm 

Joined: Mon Feb 24, 2014 4:42 pm
Posts: 1
Location: SFPUC-Hetch Hetchy Regional Water System
I have a 120/208v panel fed by (3) three single phase transformers wired together to make one 3 phase transformer can we still count this as one transformer? In this case each transformer is 37.5kVA for a total of 112.5kVA. Service is 120/208 3 phase, 4 wire. Our Electrical Engineer believes this panel is except from conducting an Arc Flash Hazard Analysis under 130.3 Exception No. 1. I disagree because of (2) which states, The circuit is supplied by one transformer. In this case it is supplied by three wired together. Three does not equal one. What say everyone?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Feb 25, 2014 7:56 am 
Sparks Level
User avatar

Joined: Tue Nov 12, 2013 6:31 am
Posts: 238
Location: Port Huron, Michigan
If you have the ability to do an arc flash study on this panel, that would be preferable to trying to find a loop hole to avoid it.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Feb 25, 2014 11:06 am 
Sparks Level
User avatar

Joined: Tue Apr 17, 2012 8:19 am
Posts: 241
Location: Charlotte, NC
Well technically a three-phase transformer is essentially 3 single-phase transformers connected together. They often share a common core.

But - I would still do the arc flash study on the panel and not be looking for a loop hole to avoid it.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Mar 10, 2014 9:59 am 

Joined: Mon Feb 22, 2010 10:24 am
Posts: 21
Larry Brilliant wrote:
I have a 120/208v panel fed by (3) three single phase transformers wired together to make one 3 phase transformer can we still count this as one transformer? In this case each transformer is 37.5kVA for a total of 112.5kVA. Service is 120/208 3 phase, 4 wire. Our Electrical Engineer believes this panel is except from conducting an Arc Flash Hazard Analysis under 130.3 Exception No. 1. I disagree because of (2) which states, The circuit is supplied by one transformer. In this case it is supplied by three wired together. Three does not equal one. What say everyone?

The guideline is written for 3 phase systems. 3 single phase transformers banked together is equivalent to 1 three phase transformer in terms of the short circuit current available. I believe the intent of the one transformer statement is to exclude multiple sources.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: 130.3 exceptions
PostPosted: Mon Jun 02, 2014 7:43 am 

Joined: Mon Jun 02, 2014 7:31 am
Posts: 1
rdj wrote:
Larry Brilliant wrote:
I have a 120/208v panel fed by (3) three single phase transformers wired together to make one 3 phase transformer can we still count this as one transformer? In this case each transformer is 37.5kVA for a total of 112.5kVA. Service is 120/208 3 phase, 4 wire. Our Electrical Engineer believes this panel is except from conducting an Arc Flash Hazard Analysis under 130.3 Exception No. 1. I disagree because of (2) which states, The circuit is supplied by one transformer. In this case it is supplied by three wired together. Three does not equal one. What say everyone?

The guideline is written for 3 phase systems. 3 single phase transformers banked together is equivalent to 1 three phase transformer in terms of the short circuit current available. I believe the intent of the one transformer statement is to exclude multiple sources.

These exceptions are all about the circuit and exception #2 "the circuit is supplied by one transformer" seems to mean anything over single phase; if not how can there be more than one transformer on a single ciruit?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: 130.3 exceptions
PostPosted: Sat Jun 07, 2014 6:46 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2174
Location: North Carolina
currently active wrote:
These exceptions are all about the circuit and exception #2 "the circuit is supplied by one transformer" seems to mean anything over single phase; if not how can there be more than one transformer on a single ciruit?


The general reason for avoiding multiple transformers on a single circuit is that if the impedances are not fairly closely matched, you will get circulating currents, and because even though you may have two transformers in parallel, if the impedances are not very, very similar, electricity flows proportional to their conductances and thus one will get much more load than the other. This is not a simple case of the capacity of two transfomers rated X and Y = X+Y.

However there are certainly cases where transformers are operated in parallel for instance for redundancy reasons such as having 3 transformers in parallel with appropriate switching to allow any given transformer to be de-energized either due to a fault or for maintenance purposes. Granted I have never seen this with low voltage (<240 V) circuits but it would not surprise me if I did see it.

Second, I have pretty much come full circle on this issue. At this point the problem I have with IEEE 1584 in its current state is that it relies on a single data point at 208 V and that the documentation stated that they could not achieve a stable arc with any of the other tests. Arcing below 250 V is really unstable and I have seen research papers showing results that are both above and below the incident energy predicted by IEEE 1584. Further as Jim Philips who is Secretary of the committee has already stated publicly, the "<125 kVA, <240 V rule" which is really little more than a passing comment has already been shown to be inadequate and that there are definitely conditions where it does not suffice. So at this point considering the original poster's condition (granted this is months later) I would suggest using the values in NESC which are based on EPRI testing for the <250 V case. NESC gives a value of 4 cal/cm^2.

In the future I am at this point of the opinion that just as with the >15 kV case, we really can't use IEEE 1584 properly for low voltage cases. OSHA reached the same conclusion recently in their findings for the updated OSHA 1910.269 Subchapter V rules for utilities for over 15 kV. This probably means that we will be using a simple "table lookup" procedure for dealing with the low voltage cases.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883