Steve Hudgik wrote:
The arc flash label must be on the equipment or device where the arc flash can happen. The point of a warning label is to let people know about the danger at the location where that danger exists.
NFPA 70E specifically requires the following types of electrical equipment, in locations other than dwellings, be marked with an arc flash warning label:
- Switchboards
- Panelboards
- Industrial control panels
- Meter socket enclosures
- Motor control centers
I've written an article about this that can be read at:The information on the arc flash label can include the upstream protective device. Just as a matter of record, NFPA70E does not specify what type of equipment has to be marked with an Arc Flash Label. NEC Article 110.16 specifies that equipment
SUCH AS (emphasis added) switchboards, Panelboards, Industrial control panels, Meter socket enclosures, Motor Control Centers. I place emphasis on "such as" because this list was not intended by NFPA70 to be all inclusive. In fact, that's why the words "such as" were added in the last code cycle.