 Post subject: Working on section adjacent to Dangerous!
PostPosted: Mon Apr 20, 2009 4:36 pm 
Sparks Level

Joined: Sat Apr 04, 2009 9:50 pm
Posts: 104
Location: San Antonio, TX
The income section of a LV switchgear (line-side of main OCPD) has a incident energy of 65 cal/cm2 (Dangerous).

The adjacent section (load side of OCPD) has a incident energy of 3 cal/cm2.

The switchgear is open frame, so there is no barriers between both sections.

What kind of label would you affix to this switchgear?

Options:

1. Only one for the whole panels (incoming and feeder sections) with the AFIE of 65 cal/cm2.
2. Dual label, for incoming section 65 cal/cm2 and for all feeder sections 3 cal/cm2.
3. Other solution.

The problem arises to be so close to a high incident energy area using only PPE of 3 cal/cm2.

Thanks.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Apr 20, 2009 5:50 pm 
Arc Level

Joined: Thu Jan 10, 2008 8:49 pm
Posts: 498
Location: New England
Without barriers you would have to use the higher rating out to an arc flash boundary that equals the lower rating.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue May 05, 2009 9:39 pm 
Sparks Level

Joined: Thu Oct 18, 2007 7:10 pm
Posts: 261
Location: NW USA
RECS wrote:
The income section of a LV switchgear (line-side of main OCPD) has a incident energy of 65 cal/cm2 (Dangerous).

The adjacent section (load side of OCPD) has a incident energy of 3 cal/cm2.

The switchgear is open frame, so there is no barriers between both sections.

What kind of label would you affix to this switchgear?

Options:

1. Only one for the whole panels (incoming and feeder sections) with the AFIE of 65 cal/cm2.
2. Dual label, for incoming section 65 cal/cm2 and for all feeder sections 3 cal/cm2.
3. Other solution.

The problem arises to be so close to a high incident energy area using only PPE of 3 cal/cm2.

Thanks.


According to some interpretations operating the main breaker would be illegal because you are above 40Cal/cm2. Working so close is probably no safer and could be more dangerous.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883