 Post subject: Labeling of MV Pad Mount Distribution Transformers
PostPosted: Mon Aug 24, 2020 8:11 am 

Joined: Mon Aug 24, 2020 7:47 am
Posts: 4
Should a pad mount medium voltage distribution transformer have two separate arc flash labels; one for the high voltage compartment (Warning Label with high voltage and low incident energy) and one for the low voltage compartment (Danger Label with low voltage and high incident energy)? Should the information be combined into a single "Danger" label that lists the higher voltage and the higher incident energy?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Labeling of MV Pad Mount Distribution Transformers
PostPosted: Mon Aug 24, 2020 11:25 am 

Joined: Thu Apr 18, 2019 11:42 am
Posts: 23
While not an answer...you might look at the supplemental information in the NESC regarding AF and pad mount transformers. AF may not be high on the secondary. Use at your discretion.

Mike

PS <link to commercial website>. Somewhat outdated but I think relevant for discussion.


Last edited by wbd on Tue Aug 25, 2020 6:09 am, edited 1 time in total.
deleted link to commercial website


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Labeling of MV Pad Mount Distribution Transformers
PostPosted: Tue Aug 25, 2020 11:39 am 

Joined: Mon Aug 24, 2020 7:47 am
Posts: 4
Hello Mike,

Thank you for the feedback. Yes, I see in NESC Table 410.1 the arc flash incident energy is substantially less for Pad Mount transformers than what the short -circuit study was indicating. Would two labels still be needed due to the different voltages associated with the high and low voltage compartments of the transformer? Gary


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Labeling of MV Pad Mount Distribution Transformers
PostPosted: Tue Aug 25, 2020 11:43 am 

Joined: Mon Aug 24, 2020 7:47 am
Posts: 4
Hello Mike, I seem to have deleted the link you provided to the website in you post. Could you please post it again. Thanks

Gary


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Labeling of MV Pad Mount Distribution Transformers
PostPosted: Tue Aug 25, 2020 2:11 pm 

Joined: Thu Apr 18, 2019 11:42 am
Posts: 23
Article by e-Hazard:
I don't like the idea of multiple labels...but may be necessary in some instances. I don't think there is an industry standard, so you get to decide the route you want to go.

Mike


Last edited by wbd on Thu Aug 27, 2020 6:31 am, edited 1 time in total.
deleted link to commercial website


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Labeling of MV Pad Mount Distribution Transformers
PostPosted: Thu Aug 27, 2020 6:37 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 825
Location: Rutland, VT
If this padmount is owned by the utility, then there should be no labels on it as it falls under OSHA 1910.269 and in the forward, OSHA discusses that it does not believe that providing labels on transmission and distribution installations is feasible or effective. Even if the padmount is customer owned, it probably falls under OSHA 1910.269 because of utility like voltages and equipment.

Since the NESC is referenced, I would think this installation is under OSHA 1910.269 for arc flash

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Labeling of MV Pad Mount Distribution Transformers
PostPosted: Thu Aug 27, 2020 3:57 pm 

Joined: Mon Aug 24, 2020 7:47 am
Posts: 4
Thank you Barry and Mike. Excellent feedback and information. Gary


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Labeling of MV Pad Mount Distribution Transformers
PostPosted: Wed Sep 02, 2020 5:31 am 

Joined: Mon Apr 06, 2015 9:51 am
Posts: 6
If it was a substation transformer with side bushings and enclosures would you label the two enclosures differently?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Labeling of MV Pad Mount Distribution Transformers
PostPosted: Wed Sep 02, 2020 6:13 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 825
Location: Rutland, VT
See above response regarding OSHA labeling for utilities.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 9 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883