There is no direct correlation between incident energy and arc blast pressure. This was identified by Dr. Ralph Lee in his original research from the late 1980s, but unfortunately a public comment was added to NFPA 70E that implied there was and at the 40 cal/cm2 incident energy level. Which happens to correlate with the old HRC 4 or now Arc Flash PPE Category 4.
Dr. Ralph Lee's research was published in the IEEE Yellow Book which is now IEEE 3007 series. You can view the graph that is included.
Danger signal pane should be at 140.1 cal/cm2 based on an employer's compliant Electrical Safety Program including a documented work task based risk assessment procedure.
Unfortunately over the last decade consulting engineers completing arc flash hazard incident energy analysis studies included an error in their reports and was propagated by the power system software vendors that wrongly automatically included a column in the "Results Table" for incident energy analysis that ≥40.0 cal/cm2 as "Dangerous" and "No PPE Exist." Both of these statements were and are false!!!!
Then the software automatically generated Danger single pane equipment labels. Software should not be used to make risk based decisions. Risk assessment is completed by the employer.
Employer's that commissioned studies were misinformed with respect to what I call the "40 cal myth!!!"
There is a lot of misinformation and disinformation related to abnormal arcing fault sustainability and arc flash published in social media, in reports issued and by "arc flash trainers." This is unfortunate.
That said employers can control the narrative related to electrical hazard identification/classification, detailed defendable risk assessment procedure and ensuring residual risk is as low as reasonably practicable by development, implementing and auditing a compliant Electrical Safety Program.
More than willing to discuss/debate this with any "arc flash trainer," consulting engineer etc. My email is
terry.becker@twbesc.ca. or call me 587 433-3777.
Electric shock leading to electrocutions (which incident statistics prove) needs attention. Also be aware of electric shock sequelae!