It is currently Mon Nov 23, 2026 5:08 am



Post new topic Reply to topic
Author Message
 Post subject: Labeling Requirement for DC Voltage
PostPosted: Wed Dec 31, 2025 9:38 pm 

Joined: Wed Feb 26, 2025 1:07 am
Posts: 2
Greetings,

I couldn't find clear information regarding DC equipment labeling in NFPA 70E. Specifically, I am looking for the voltage range that requires an arc flash study.

Thx


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Labeling Requirement for DC Voltage
PostPosted: Fri Jan 02, 2026 4:42 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
T130.5(C) - Under 125V AC or DC no likelihood of occurrence. Over that, then yes, you should be labeling.

The rest of Art. 130 has information on labeling and PPE for AC and DC systems. 130.5(H) has labeling requirements and doesn't distinguish between AC and DC.

T130.7(C)(15)(b) it the table for using the Category method for DC systems and 130.7(C)(15)(c) shows the PPE per category and does not distinguish between AC and DC systems.

Recommend you review Art 130 completely rather than take my cherry-picked code citations as gospel.

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883