I was in a discussion today about 70e, section 130.3 Arc Flash Hazard Analysis. I was told that if we use tables instead of the full analysis (Exception 2 of 130.3) then 130.3 (C) Equipment Labeling does not apply. I'm reading it as we can do EITHER the full analysis OR use the exception to use the tables (if they apply to the equipment) but that the labels called for in 130.3 (C) must be applied in either case. It does not seem right to me that we would have panels without the info needed to select PPE.

Thanks,

Ed


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Dec 07, 2009 2:50 pm 
Sparks Level

Joined: Sun Dec 23, 2007 1:44 pm
Posts: 348
Location: Charlotte, NC
The labelling requirements do not change if you use the tables.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Dec 07, 2009 9:59 pm 
Arc Level

Joined: Thu Jan 10, 2008 8:49 pm
Posts: 498
Location: New England
Read the NEC 110.16.
While NFPA 70E is NOT law in OSHA, almost all States adopt the NEC for building codes. So 110.16 is probably part of your State law.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Dec 09, 2009 9:33 am 
Sparks Level

Joined: Fri May 01, 2009 9:10 am
Posts: 73
Do Analysis

Imagine the extended downtime involved if each electrician had to go consult NFPA 70E Table 130 prior to each job. Labeling equipment saves $$$ in the long run. I also recommend a detailed analysis as the tables tend to be very conservative. As for the NEC 110.16... labeling for arc flash hazards hasn't been around that long so some want to fall back and be "grandfathered". OSHA requires analysis and labeling which are not "grandfather-able" if that's a word.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Dec 13, 2009 2:24 am 

Joined: Sun Nov 22, 2009 8:53 pm
Posts: 1
Location: IL
fangle1948 wrote:
Hi,

I was in a discussion today about 70e, section 130.3 Arc Flash Hazard Analysis. I was told that if we use tables instead of the full analysis (Exception 2 of 130.3) then 130.3 (C) Equipment Labeling does not apply. I'm reading it as we can do EITHER the full analysis OR use the exception to use the tables (if they apply to the equipment) but that the labels called for in 130.3 (C) must be applied in either case. It does not seem right to me that we would have panels without the info needed to select PPE.

Thanks,

Ed


You must work at the same place that I do! :D

I am in the same exact scenario as you are and I have the same opinion as you do.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Dec 14, 2009 4:39 am 

Joined: Tue Dec 01, 2009 11:06 am
Posts: 9
The other side to the discussion called the NFPA to get clarification. The correct answer is as was suggested here - you can use the analysis OR the tables, but either way you must label. Exception 2 does not exclude labeling.

Thanks to all for the help!

Ed


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883