Post subject: Arc Flash Incident Fused Disconnect Switch Posted: Mon Jul 22, 2019 5:51 am |
|
Plasma Level |
 |
Joined: Wed May 07, 2008 5:00 pm Posts: 879 Location: Rutland, VT
|
|
Top |
|
 |
Leonard
|
Post subject: Re: Arc Flash Incident Fused Disconnect Switch Posted: Mon Jul 29, 2019 4:58 am |
|
Joined: Tue Jul 01, 2014 8:40 am Posts: 110
|
Hi Barry Greetings from North of the border. Yes it is plenty warm up here  I was wondering if I could please have your clearance permission to reproduce your post with the photos? They will be strictly used for training purposes up here and I would like to insert into my next monthly newsletter Thanks Barry Best regards Len Cicero Burlington, Ontario
|
|
Top |
|
 |
Robertefuhr
|
Post subject: Re: Arc Flash Incident Fused Disconnect Switch Posted: Mon Jul 29, 2019 8:37 am |
|
Sparks Level |
 |
Joined: Tue Oct 26, 2010 5:00 pm Posts: 201 Location: Maple Valley, WA.
|
This accident is a perfect example of what I talk about in our Electrical Safety Seminars. I always ask the electricians if they or one of their co-workers have ever experienced electrical equipment having a short circuit or arc flash event. Almost all say "yes". Luckily, electrical equipment is very reliable but even brand new equipment can fail.
Always be prepared for that "Electrical Bomb" to go off.
I was glad to hear that the operator of the switch was standing off to the side. We stress this as well in our classes. Doors rarely contain a large arc flash event unless the equipment is arc flash resistant MCCs or Switchgear.
_________________ Robert Fuhr, P.E.; P.Eng. PowerStudies
|
|
Top |
|
 |
Highkvs
|
Post subject: Re: Arc Flash Incident Fused Disconnect Switch Posted: Tue Aug 06, 2019 1:42 pm |
|
Joined: Mon Jul 14, 2014 9:23 am Posts: 8
|
The root cause of this electrical explosion was a result of the switch being installed incorrectly a violation of the national electric code. An inspection of the original installation would have revealed incorrect bending radius and routing of wiring internal to the switch enclosure. Applicable electrical standards require equipment maintenance, maintenance allows for visual inspection of conditions likely to lead to failure. Just as switches have been damaged by installation at locations outside of their UL listings and failed, The switch mechanism itself and the enclosure appear to have functioned as designed and listed.
This incorrect installation is why the electrical safet standards requires work involving operation of energized electrical equipment be evaluated and assessed for potential dangers before the work takes place.
Shame on the original installer and a caution to users of electrical equipment that they must remain aware of the condition of their installed electrical equipment, after the contractor has left. Was this installation inspected , not very well.
|
|
Top |
|
 |
stevenal
|
Post subject: Re: Arc Flash Incident Fused Disconnect Switch Posted: Wed Aug 07, 2019 7:43 am |
|
Joined: Tue Jan 13, 2009 5:00 pm Posts: 606
|
Is that a factory knockout? There are others that appear to be in more appropriate locations.
|
|