PostPosted: Sun Feb 21, 2016 12:29 pm
A variation of this week's question was asked many years ago but study methods continue to evolve. IEEE 1584 - 2002 provides a table for suggested working distance to be used for the incident energy calculations. The distances are:
18 inches - Low Voltage MCCs and Panels
24 inches - Low Voltage Switchgear
36 inches - 5 kV and 15 kV Switchgear
Here is this week's question
Yes
No
Something else
Feel free to give us your thoughts about the working distance.