Should there be an arc flash label on or near DC battery racks?
Yes – we label on/near rack 63%  63%  [ 19 ]
No – we don’t label on/near the rack 27%  27%  [ 8 ]
No Battery Racks 10%  10%  [ 3 ]
Total votes : 30
 Post subject: DC Arc Flash Labels / Battery Racks
PostPosted: Sun May 14, 2017 12:58 pm
This week’s question has come up on several occasions.
Since arc flash labels are showing up more on DC equipment, should there be a label on or near dc batteries / battery racks?
No – we don’t label the rack
No Battery Racks
 Post subject: Re: DC Arc Flash Labels / Battery Racks
PostPosted: Mon May 15, 2017 9:42 am
Usually, there will be a fused disconnect switch or circuit breaker that is located near the Battery Racks. When there is one, we will label this disconnect or CB (using the Line Side Option) but not the battery rack. If there is no switch or CB near by, then we will provide a label for the battery rack.