It is currently Thu Oct 22, 2020 8:39 pm
Have you used 4 cal/cm^2 from NESC Table 410-1 for panels up to 250V?
Yes
No
Never heard of it
You may select 1 option
View results
 Post subject: Maximum 4 cal/cm^2 for panels to 250 Volts? NESC 410-1
PostPosted: Sun Oct 11, 2020 11:30 am
The 2017 Edition of the National Electrical Safety Code (IEEE C2) contains Table 410-1 Clothing and clothing systems for voltages 50 V to 1000V (ac).
This table lists the maximum arc rating necessary for protection from the arc flash hazard based on equipment type.
4 cal/cm^2 is listed for panelboards 50V to 250 V
Note (1) [applies to entire table]
This table was developed from fault testing based on equipment type and is independent of fault current unless otherwise noted.
Note (2) [specific 50 V – 250 V panelboards]
The arc rating values for the panels are based on industry testing by two separate major utilities and one research institute and that the arc will not sustain more than 2 cycles.
This week’s question:
Yes
No
Never heard of it
Report this post
 Post subject: Re: Maximum 4 cal/cm^2 for panels to 250 Volts? NESC 410-1
PostPosted: Mon Oct 12, 2020 7:38 am
Note the scope of the NESC prior to use. It may not be appropriate for many forum members.
Report this post
PostPosted: Mon Oct 12, 2020 7:59 am
To add to the discussion: OSHA letter of interpretation
Report this post
You can post new topics in this forum
You can reply to topics in this forum