What method do you use for 3 Phase Arc Flash Studies < 15 kV?

_________________
Jim Phillips, P.E.
Brainfiller.com


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Aug 08, 2010 8:10 pm 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
I voted IEEE 1584, but it needs to be qualified. We don't use IEEE 1584 for all < 15 kV analyses. For overhead medium voltage distribution (>1 kV), we use ARCPRO software.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Aug 09, 2010 6:41 am 
Sparks Level

Joined: Sun Dec 23, 2007 1:44 pm
Posts: 348
Location: Charlotte, NC
Same comment as jghrist, but it is considered a single phase event.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Aug 09, 2010 7:49 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1637
Location: Scottsdale, Arizona
I probably could have been more clear about this. I meant for 3 Phase systems.

This is the first of what will likely be a weekly or bi-weekly survey question. It should help everyone see what the "industry norm" is for certain issues. - At least the norm according to the forum users.

Thanks Everyone!

_________________
Jim Phillips, P.E.
Brainfiller.com


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Aug 09, 2010 8:01 am 

Joined: Fri Sep 05, 2008 8:10 am
Posts: 36
We are using the NFPA 70E tables as a starting point until a full software analysis can be performed.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Aug 09, 2010 11:26 am 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
brainfiller wrote:
I probably could have been more clear about this. I meant for 3 Phase systems.

We use ARCPRO for 3Ø overhead systems. We only consider 1Ø faults.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Aug 09, 2010 3:52 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1637
Location: Scottsdale, Arizona
jghrist wrote:
We use ARCPRO for 3Ø overhead systems. We only consider 1Ø faults.


So much for making a quick post when rushing off the airport this morning. Yes, I meant 3 phase arc flash modeling.

_________________
Jim Phillips, P.E.
Brainfiller.com


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Aug 12, 2010 3:52 pm 
Sparks Level

Joined: Mon Dec 14, 2009 4:24 pm
Posts: 61
Ieee 1584.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Aug 13, 2010 8:29 am 

Joined: Tue Feb 16, 2010 7:59 am
Posts: 21
Location: Minneapolis, MN
Gentlemen,
Thanks for the feedback.
Jim, this is a great idea. Keep the surveys comming.

Bob Ragsdale P.E.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Oct 06, 2010 9:56 pm 
Sparks Level

Joined: Thu Oct 18, 2007 7:10 pm
Posts: 263
Location: NW USA
Our software is based on IEEE 1584 and that is what we use as an industry standard.

It would be interesting if anyone is using NFPA 70E calculations for systems above 600V, I don't believe that is recommended anymore.


Report this post
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 10 posts ] 

All times are UTC - 7 hours


You can post new topics in this forum
You can reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883