Do you use the "2 second cut off rule"?
Yes
No
Sometimes - it depends on the situation
We use a different time (please post what is used)
You may select 1 option

View results
Author Message
 Post subject: Do you use the "2 Second Cut Off Rule"?
PostPosted: Mon Aug 23, 2010 4:09 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1637
Location: Scottsdale, Arizona
When a time current curve indicates the arc flash duration is considered long, do you use the 2 second cut off as discussed in IEEE 1584 Annex B.1.2? (provided there is sufficient room for escape?)

_________________
Jim Phillips, P.E.
Brainfiller.com


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Oct 06, 2010 9:57 pm 
Sparks Level

Joined: Thu Oct 18, 2007 7:10 pm
Posts: 263
Location: NW USA
Upon initial calculations we had some 480V transformers with unbelievable approach distances; using 2 second cutoff made the results more credible.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Nov 10, 2010 8:00 pm 
User avatar

Joined: Mon Nov 05, 2007 10:10 am
Posts: 48
Location: Mid-West
Application Specific

I believe this is applicaiton specific. We recently evaluated a short cirucit / coordination / arc flash study that was completed for a client by a third party, and one thing caught my eye. They utilized the two second rule. For the application I thought this may be a bad Idea would like to get your thoughts.

Design intent:
EE locally laied out a system of a bus duct mounted 45' above the floor adjacent to a catwalk. The bus plug was caculated at a level 3 utilizing the two second rule. Without the two second rule the breaker clearing time was upwards of 8-10 seconds (seems like an eternity to me).

Some argued that after two seconds the "arc" would not be able to re-strike. I am still struggling with this one, however.

My concern where do you go on a catwalk? Bigger concern the blast pressure was estimated somewhere at 16K per sq. ft. meaning that if there was an incident it may be the fall that causes a fatal injury from 45' up. As it turns out by changing some settings on the main breaker trip unit (taking out the I^2 and setting the short time lower) it picked up the fault exponentially faster at the 85% or worst case level, and still provided good coordination with downstream devices. It was amazing what a couple of setting changes can make.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Mar 11, 2011 12:28 pm 

Joined: Mon Feb 07, 2011 9:45 am
Posts: 7
Is there a voltage limitation on the 2 second rule? Presently our company standard it to us 5 seconds for above 1000 volts.

Thanks.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Mar 11, 2011 8:46 pm 
Sparks Level

Joined: Mon Mar 29, 2010 5:02 am
Posts: 136
2 seconds in the electrical world is HUGE......


Report this post
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You can post new topics in this forum
You can reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883