Do you use the normal fault current only or consider alternate scenarios?
Normal Short Circuit Current Only
Consider Alternate Scenarios
None of the above
You may select 1 option

View results
Author Message
 Post subject: Utility Short Circuit Current
PostPosted: Sun Aug 29, 2010 4:00 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1637
Location: Scottsdale, Arizona
When performing an arc flash calculation study do you use the normal condition fault current only or do you also look at alternate scenarios such as minimum or maximum fault current?

_________________
Jim Phillips, P.E.
Brainfiller.com


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Aug 30, 2010 8:42 am 
Sparks Level

Joined: Sun Dec 23, 2007 1:44 pm
Posts: 348
Location: Charlotte, NC
I voted that we consider alternate scenarios, but this is for (NESC) OH utility distribution lines where work will be performed at locations certainly other than the substation bus.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Oct 06, 2010 9:53 pm 
Sparks Level

Joined: Thu Oct 18, 2007 7:10 pm
Posts: 263
Location: NW USA
I have manipulated the local PUD substation power transformers on and off line (only within the software :p ) to affect highest and lowest available fault current. This did not affect most locations on this particular study buy perhaps a dozen out of 400 busses increased arc flash exposure when fault current was lowest.

Most locations I would not have access to information to do this but at this one spot I had previously completed work for the PUD.


Report this post
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You can post new topics in this forum
You can reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883