Arc Flash Forum
Maintenance Settings
https://brainfiller.com/arcflashforum/viewtopic.php?f=33&t=1314
Page 1 of 1
Author:  Jim Phillips (brainfiller) [ Mon Oct 04, 2010 1:52 am ]
Post subject:  Maintenance Settings
As part of the results of an arc flash study, have you begun recommending or implementing “temporary” maintenance settings anywhere to reduce the incident energy while energized work is being performed?
Author:  Zog [ Mon Oct 04, 2010 5:41 am ]
Does that include devices such as Quick Trip?
Author:  Jim Phillips (brainfiller) [ Mon Oct 04, 2010 6:39 am ]
Didn't mean for it to. Just meant temporarily change IP from Hi to Low or similar setting change.
Many use this (at least as a recommendation) but a surprising number do not since they do not want to complicate procedures and / or leave this up to others to lower and then remember to restore the original setting.
Author:  Zog [ Mon Oct 04, 2010 7:24 am ]
Exactly, which is why I don't recommend maintenence settings. Using a maintenence switch allows for control when you have a padlockable switch.
Procedure is then simplified, usually a second label is used for PPE requirements when system is enabled.
Author:  Jim Phillips (brainfiller) [ Mon Oct 04, 2010 11:04 am ]
Yep and I think this survey question's results are quickly pointing that out.
Thanks!
Author:  Gary B [ Wed Oct 06, 2010 9:43 pm ]
Have not done this because it remains a customer choice and my customers have not chosen this.
Greatest concern is a nuisance trip because the switch might inadvertently be left in maintenance mode.
Author:  mahan4 [ Thu Oct 07, 2010 12:32 pm ]
It will typically confuse the client and we should avoid complication in safe work practices, however sometimes it is necessary, for instance when HRC is 4, client might prefer to bring down the HRC via adjusting settings than to wear a category 4 suit
Author:  stevenal [ Fri Oct 08, 2010 9:04 am ]
On the utility side we combine an instantaneous setting with non-reclose. Easy to do with microprocessor relays, and we have been doing so well before arc flash requirements came to the NESC. No extra training needed since reclosing is routinely disabled during hot line work and re-enabled after.
Author:  stefancb4 [ Thu Nov 11, 2010 5:14 pm ]
Report recommendations
We report busses that have IE greater than Category 3 and where static trip breakers exist, we recommend the use of maintenance settings.
http://www.phpbb.com/
