 Post subject: Working Distance
PostPosted: Sun Oct 24, 2010 10:45 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
Do you use the standard 18, 24 and 36 inch working distances from IEEE 1584 or do you use something else for the IEEE based arc flash calculations?

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Dec 29, 2010 9:06 pm 
Sparks Level

Joined: Thu Oct 18, 2007 7:10 pm
Posts: 262
Location: NW USA
Previously standardized on 24" working distance, but recently conformed to IEEE 1584 defaults for liability reasons. Considering the potential for mistakes and misunderstanding, I think we gave up more than we gained: 24" was a reliable standard easy to understand and with no mistakes on the labels.


Top