| Minimum Arc Rating of Protective Clothing and PPE https://brainfiller.com/arcflashforum/viewtopic.php?f=33&t=1404 |
Page 1 of 1 |
| Author: | Jim Phillips (brainfiller) [ Mon Nov 22, 2010 2:26 am ] |
| Post subject: | Minimum Arc Rating of Protective Clothing and PPE |
What is the minimum arc rating (cal/cm2) of protection that you and/or personnel at your company wear? |
| Author: | gastoor [ Thu Dec 16, 2010 7:51 am ] |
| Post subject: | |
Electrical Lead On our arc flash labels, it is stated at 18", but we have down to .4 at 18" up to 182.7 for extreme danger cases. PPE only up to CAT4. |
| Author: | Gary B [ Wed Dec 29, 2010 8:56 pm ] |
| Post subject: | |
Risk category 1 or risk category 2 to enter that plant ( two different locations with different policy) and then a fully rated arc flash suit (above 40 cal/cm2) to put on when encountering any higher than RC 1 switchgear. |
| Author: | MIEngineer [ Mon Jan 03, 2011 7:14 am ] |
| Post subject: | |
We are requiring non-melting clothing minimum. Coveralls rated HRC 2 and faceshields/balacalava available when required. Also HRC 4 suit and related equipment available when needed. I should add this is a facility with the majority of equipment 2 or less. |