Arc Flash Forum
https://brainfiller.com/arcflashforum/

Current Limiting Devices
https://brainfiller.com/arcflashforum/viewtopic.php?f=33&t=1483
Page 1 of 1

Author:  Jim Phillips (brainfiller) [ Sun Jan 09, 2011 6:05 pm ]
Post subject:  Current Limiting Devices

Do you use current limiting devices to reduce the arc flash incident energy?

Author:  Oliche121 [ Mon Jan 17, 2011 1:56 am ]
Post subject: 

Which current limiting products to reduce arc Flash risk ??

Which current limiting products are allowed for arc flash reduction ?
Do they request to succed some tests ?

Author:  haze10 [ Mon Jan 17, 2011 10:54 am ]
Post subject: 

Current Limiting Fuses and Breakers reduce the let through fault current. By reducing the fault current, you reduce the Incidend Energy (arc flash).

Author:  Jim Phillips (brainfiller) [ Mon Jan 17, 2011 2:24 pm ]
Post subject: 

Oliche121 wrote:
Which current limiting products are allowed for arc flash reduction ?
Do they request to succed some tests ?


IEEE 1584 did some testing with current limiting fuses and published a few equations. Properly applied C.L. breakers and fuses can significantly reduce the incident energy.