 Post subject: Working Distance for Labels on the Back of Equipment
PostPosted: Sun Mar 27, 2011 7:34 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1637
Location: Scottsdale, Arizona
This next question is a follow up on an earlier poll question about labeling the back of equipment. Since the bus is typically towards the rear, the distance from a prospective arc flash would technically be closer from the back than from the front.

Here is the question:


If you label the back of equipment such as switchgear, do you use the same working distance as the label on the front of the equipment?
  • Yes we use the same label and working distance
  • No we modify the working distance.
  • Uh oh, we never thought about it.
  • We do not label the back of any equipment.

_________________
Jim Phillips, P.E.
Brainfiller.com


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Mar 28, 2011 6:14 am 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
It depends on whether the back of the equipment would be opened for work or inspection. On MV metal clad switchgear, cable entrances are usually in the rear and may be accessed. We have calculated incident energy at both 36" (standard for switchgear) and 18" (used for cable entrance).

For switchgear where access to the back requires removing panels instead of opening doors, I wouldn't label it any differently.

I suspect the answer would be "never thought about it" in many cases. I started a thread on 12/17/10 on this subject but got zero responses. http://www.arcflashforum.com/showthread.php?t=1437


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Mar 28, 2011 6:28 am 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 551
Location: Wisconsin
Depends on the construction of the equipment.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jun 14, 2011 7:49 am 
Sparks Level

Joined: Thu Oct 18, 2007 7:10 pm
Posts: 263
Location: NW USA
Use the same label, with default IEEE 1584 working distances based on equipment type and voltage. There might be a liability in reinterpreting an industry standard.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jun 14, 2011 11:23 am 

Joined: Mon Jan 26, 2009 5:00 pm
Posts: 46
Location: Midwest
IMO it depends on the construction of the equipment.

As far as distances, I rely on the default numbers in 1584 for gap and working distance.

The biggest difference between front and back, especially in the switchgear example seems to be the compartmentalization. The rear with cable connections may be eligible to utilize the upstream device for fault clearing, whereas the front may not.


Report this post
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You can post new topics in this forum
You can reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883