 Post subject: 85% Arcing Current
PostPosted: Sun Apr 17, 2011 5:52 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1635
Location: Scottsdale, Arizona
IEEE 1584 suggests that an additional incident energy calculation should be performed using 85% of the arcing current for systems less than 1000 volts. This is to determine if the upstream protective device will still trip instantaneously during an arc flash.

Do you use the 85% value as part of your calculations?

Yes - we use 85% as well as 100%
No - we only use 100%
Other - we use a value other than 85%

_________________
Jim Phillips, P.E.
Brainfiller.com


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Jun 01, 2011 11:16 am 

Joined: Sat Nov 20, 2010 10:17 am
Posts: 13
Location: Victoria British Columbia
Yes - we use 85% as well as 100% .

We are mostly concerned with low voltage 450 Volt used on Navy ships. It has made significant diferences in some cases. 27 Cal/cm² vice 8

Jim


Report this post
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You can post new topics in this forum
You can reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883