Overcurrent Device Maintenance
https://brainfiller.com/arcflashforum/viewtopic.php?f=33&t=1686
Page 1 of 1

Author:  Jim Phillips (brainfiller) [ Sun Apr 24, 2011 5:41 pm ]
Post subject:  Overcurrent Device Maintenance

NFPA 70E Section 205.3 General Maintenance Requirements. Overcurrent protective devices shall be maintained in accordance with the manufacturers’ instructions or industry consensus standards.

When is the last time you or your client tested/calibrated/maintained the overcurrent protective devices? (those that can be tested)

  • Every year
  • Every 2-3 years
  • Every 4-5 years
  • Greater than 5 years
  • Never been done that I know of

Author:  richxtlc [ Mon Apr 25, 2011 7:59 am ]
Post subject: 

I have clients that are all over the spectrum, from every year to don't know when it was tested. I have one client who had a two out of three bus configuration with all three circuit breakers closed and could not tell me how long it had been that way. It was soon corrected and back to its design configuration.

Author:  C. Harman [ Tue May 03, 2011 10:38 am ]
Post subject: 

Depends. SOme relays are tested every three years as part of the nerc compliance. Others do not have regular testing.

Author:  Capt Jim [ Tue May 03, 2011 4:44 pm ]
Post subject: 

Relay Testing

If we are talking about consumer substations. NFPA 70b--2010 edition (page 250) recommends a inspection/test frequency of 1-2 years for induction disc relays and 3 years for solid state relays.
Any relays that misoperation may impact the distribution system are dictated by the utility
Any relays that misoperation may affect the power transmission and bulk distribution system are dictated by the local Power Authority.