If you find overdutied equipment during an arc flash study, for labeling you would:
Label the overdutied equipment and ignore the inadequacy
Label the overdutied equipment and list the inadequacy in the report
Do not label the equipment - list the inadequacy in the report
Stop the study until the inadequacy is addressed
Something else - please comment.
You may select 1 option

View results
Author Message
 Post subject: Overdutied Equipment
PostPosted: Sun Jun 05, 2011 4:36 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1479
Location: Scottsdale, Arizona
This week’s question has been frequently discussed within the IEEE committee. I thought it would be interesting to see how others handle the situation.

During the course of performing an arc flash study, what if you discover equipment that has an inadequate interrupting or withstand rating. As far as arc flash warning labels and the arc flash study are concerned, you:

  • Label the equipment and do nothing about the inadequacy (not in scope)
  • Label the equipment AND list the inadequacy in the report
  • Do not label the equipment AND list the inadequacy in the report
  • Stop the study until the inadequacy is addressed
  • Something else

_________________
Jim Phillips, P.E.
Brainfiller.com


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Jun 06, 2011 8:14 am 

Joined: Sat Mar 19, 2011 6:13 pm
Posts: 14
I will include something in the executive summary, in bold letters, similar to this:

It should be noted that the following equipment and/or protective devices are rated below the available fault current at their location. A fault event affecting any of these could cause catastrophic damage to the equipment and risk the safety of personnel nearby. In addition, it could result in a lengthy power outage that could affect the facility's operation.

When doing a study, I consider myself as a messenger only. It is up to the facility management to decide how they act on the recommendations.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Jun 24, 2011 7:16 am 

Joined: Tue Feb 16, 2010 7:59 am
Posts: 21
Location: Minneapolis, MN
Forgive me for answering a question with another question but, having been to a number of facilities where no attention was paid to interrupting capacities, I feel this question begs another question. Consider the following scenarios.

Panel P-1 has bolted fault of 45 kA and has CB’s rated at 25 kAIC. One of these circuit breakers feed Panel P-2 where:

1) Bolted fault and arcing fault at P-2 are < 25kA.
2) Bolted fault at P-2 >25kA and arcing fault < 25kA.
3) Bolted fault and arcing fault at P-2 >25kA.

Some will label scenario 1 and list it as a deficiency in the report but scenarios 2 & 3 are a lot more dangerous. My answer is “it depends”.

Bob Ragsdale, P.E.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Jun 24, 2011 1:14 pm 

Joined: Sun Oct 05, 2008 5:00 pm
Posts: 17
BCR_1962 wrote:
Forgive me for answering a question with another question but, having been to a number of facilities where no attention was paid to interrupting capacities, I feel this question begs another question. Consider the following scenarios.

Panel P-1 has bolted fault of 45 kA and has CB’s rated at 25 kAIC. One of these circuit breakers feed Panel P-2 where:

1) Bolted fault and arcing fault at P-2 are < 25kA.
2) Bolted fault at P-2 >25kA and arcing fault < 25kA.
3) Bolted fault and arcing fault at P-2 >25kA.

Some will label scenario 1 and list it as a deficiency in the report but scenarios 2 & 3 are a lot more dangerous. My answer is “it depends”.

Bob Ragsdale, P.E.


We've wrestled with this one too. I have heard of some that just stop at the first inadequate panel and won't label anything past it. Others only leave the label off the equipment that is inadequate and continue to label beyond. Not sure what the answer is but you are correct, it would be great to hear other opinions. The original poll question was great. Let's carry it further.

Thanks!


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Aug 31, 2011 4:19 pm 

Joined: Wed Aug 31, 2011 3:33 pm
Posts: 14
Location: Denver, CO
Supplemental label?

It is being discussed to supply an additional label to warn of the overdutied equipment. I know NEC 110.16 only requires arc-flash label, but NEC is usually minimal requirement.


Report this post
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You can post new topics in this forum
You can reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883