Do you use an Energized Electrical Work Permit for Replacing Fuses?
No - we consider this “troubleshooting”
Yes - we create an EEWP for each case
Yes - we have a standing EEWP for this task
You may select 1 option

View results
Author Message
 Post subject: Fuse Replacement and EEWP
PostPosted: Sun Jun 12, 2011 2:15 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1635
Location: Scottsdale, Arizona
This week’s question is from a discussion on the forum last week.

When replacing / removing / inserting fuses, do you require an energized electrical work permit (EEWP)?
[INDENT]
  • No - we consider this “troubleshooting”
  • Yes - we create an EEWP for each case
  • Yes - we have a standing EEWP for this task
[/INDENT]

_________________
Jim Phillips, P.E.
Brainfiller.com


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Jun 12, 2011 10:24 pm 
Sparks Level

Joined: Mon Mar 29, 2010 5:02 am
Posts: 136
One of the clients I work with would put fuse replacement under a "480 volt troubleshooting" standard permit or the "24 volt troublshooting" standard, depending on the system... These are both energized work.. Most other places would call it "cold work"...


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Jun 13, 2011 9:43 am 
Sparks Level

Joined: Wed Oct 29, 2008 6:06 am
Posts: 136
Location: Michigan
If the task requires the qualified associate to install, remove or replace components/conductors, the work is then not diagnostic in nature and must be covered by an EEWP or the equipment must be placed in an electrically safe work condition.

In the vast majority of cases after troubleshooting we de-energize for repairs since we cannot meet the justification of greater hazard or infeasibility. Sometimes it is inconvenient; however, it drives better equipment design and safer work practices. We do however permit resetting circuit breakers, overloads, drives, etc. to be performed without an EEWP, providing that appropriate safe work practices and PPE are used.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Jun 13, 2011 10:37 am 
Sparks Level

Joined: Mon Mar 29, 2010 11:52 am
Posts: 110
Location: Yankton SD/ Lead SD
If you are replacing a fuse the equipment is not running. Therefore, why not just shut down the line side feeder, verify an electrically safe working condition, replace the fuse and re-energize the system. No EEWP needed for that.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Jun 13, 2011 8:42 pm 
Sparks Level

Joined: Mon Mar 29, 2010 5:02 am
Posts: 136
cbauer wrote:
If you are replacing a fuse the equipment is not running. Therefore, why not just shut down the line side feeder, verify an electrically safe working condition, replace the fuse and re-energize the system. No EEWP needed for that.


Assuming you did some troubleshooting before just replacing it..Are you troubleshooting it live?


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jun 14, 2011 4:00 am 
Sparks Level

Joined: Mon Jul 26, 2010 10:55 am
Posts: 67
None of the above

For the most part we cannot justify the need for an EEWP. Our real issues come in where we have fused switches in and MDP and we really don't want to shut down a building or buildings to preform a task that in my NON PE opinion is not likely to be any more hazardous than actually being in the room with the gear. To say that this work is hazardous is an extreme stretch in my opinion. I know what I believe the code says and we will continue to follow that until something changes but this is an area were I either need to be "schooled" or something needs to be changed.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jun 14, 2011 8:23 am 
Sparks Level

Joined: Mon Mar 29, 2010 11:52 am
Posts: 110
Location: Yankton SD/ Lead SD
glen1971 wrote:
Assuming you did some troubleshooting before just replacing it..Are you troubleshooting it live?


Yes troubleshoot systems live. But troubleshooting does not require an EEWP.


Report this post
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


You can post new topics in this forum
You can reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883