It depends on whether the back of the equipment would be opened for work or inspection. On MV metal clad switchgear, cable entrances are usually in the rear and may be accessed. We have calculated incident energy at both 36" (standard for switchgear) and 18" (used for cable entrance).
For switchgear where access to the back requires removing panels instead of opening doors, I wouldn't label it any differently.
I suspect the answer would be "never thought about it" in many cases. I started a thread on 12/17/10 on this subject but got zero responses.
http://www.arcflashforum.com/showthread.php?t=1437