How do you comply with NEC 240.87 Non-instantaneous
We never specify devices without an instantaneous
Zone-selective interlocking
Differential Relaying
Maintenance Switch
Something else (please comment)
You may select up to 5 options

View results
Author Message
 Post subject: Non-instantaneous Trip and NEC 240.87
PostPosted: Sun Jul 03, 2011 3:39 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1637
Location: Scottsdale, Arizona
240.87 Noninstantaneous
Where a circuit breaker is utilized without an instantaneous trip, one of the following or approved equivalent means shall be provided:
[INDENT](1) Zone-selective interlocking
(2) Differential Relaying
(3) Energy-reducing maintenance switching with local status indicator.
[/INDENT]Do you use protective devices without an instantaneous as part of the design and if so, what changes (if any) have you made to comply with this article?
[INDENT]
  • We never specify devices without an instantaneous trip.
  • Zone selective interlocking
  • Differential Relaying
  • Maintenance Switch
  • Something else (please comment)
[/INDENT]Select all that apply.

_________________
Jim Phillips, P.E.
Brainfiller.com


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Jul 04, 2011 3:12 pm 

Joined: Sat Jul 07, 2007 5:00 pm
Posts: 10
We have not had a design with L,S only (no Instantaneous) since the 2011 NEC came out. The next time we do, we will likely specify a maintenance switch. Seems like the simpler approach.


Report this post
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You can post new topics in this forum
You can reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883