| Author: | Jim Phillips (brainfiller) [ Sun Jul 03, 2011 3:39 pm ] |
| Post subject: | Non-instantaneous Trip and NEC 240.87 |
240.87 Noninstantaneous Where a circuit breaker is utilized without an instantaneous trip, one of the following or approved equivalent means shall be provided: [INDENT](1) Zone-selective interlocking (2) Differential Relaying (3) Energy-reducing maintenance switching with local status indicator. [/INDENT]Do you use protective devices without an instantaneous as part of the design and if so, what changes (if any) have you made to comply with this article? [INDENT]
|
|
| Author: | J Scott [ Mon Jul 04, 2011 3:12 pm ] |
| Post subject: | |
We have not had a design with L,S only (no Instantaneous) since the 2011 NEC came out. The next time we do, we will likely specify a maintenance switch. Seems like the simpler approach. |
|