| Author: | Jim Phillips (brainfiller) [ Sun Jul 17, 2011 3:23 pm ] |
| Post subject: | Motor Contribution and Arc Flash Studies |
When performing an Arc Flash Hazard Calculation Study, IEEE 1584 suggests including all motors 50 hp (37 kW) and larger in the model to account for motor short circuit current contribution. For motors that can contribute short circuit current, do you:
|
|
| Author: | JBD [ Mon Jul 18, 2011 8:34 am ] |
| Post subject: | |
We include motors greater than 50HP, but we also run arc flash scenarios with no motors running. |
|
| Author: | David S. [ Tue Jul 19, 2011 9:28 am ] |
| Post subject: | |
We typically use SKM to calculate Arc Flash values. Since SKM has the ability to calculate all motor faults, we use it; it is more conservative than only considering >50hp motors. |
|
| Author: | joebell [ Sun Jul 24, 2011 5:58 am ] |
| Post subject: | |
Why does IEEE 1584 suggest all 50 hp motors and larger be included ? Would 2 25 hp motors add the same contribution? |
|