Based on the 2012 NFPA 70E, what will you put on labels to define PPE requirements?
Incident Energy ONLY 3%  3%  [ 1 ]
Arc Rating ONLY 9%  9%  [ 3 ]
PPE Level ONLY 6%  6%  [ 2 ]
HRC Only 6%  6%  [ 2 ]
BOTH Incident Energy AND Arc Rating 9%  9%  [ 3 ]
BOTH Incident Energy AND Level 69%  69%  [ 24 ]
A Different Combination (please elaborate) 0%  0%  [ 0 ]
Total votes : 35
Author Message
 Post subject: Labels and the 2012 NFPA 70E
PostPosted: Sun Oct 23, 2011 3:55 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
Arc flash warning label requirements continue to evolve. Here is a brief history from 2004 through 2012.

2004 Edition
Just a basic warning label

2009 Edition
Warning label with either the available incident energy or the required level of PPE

2012 Draft - not used
Warning label with either the available incident energy or the minimum arc rating of clothing along with the date of the analysis, nominal system voltage and the arc flash boundary.

2012 Edition of NFPA 70E is finally here and the new requirements are:

Pick at least one:
  • Available incident energy and the corresponding working distance
  • Minimum arc rating of clothing
  • Required level of PPE
  • Highest Hazard/Risk Category (HRC) for the equipment
And:
  • Nominal system voltage
  • Arc flash boundary

Exception: Labels applied prior to September 30, 2011,
are acceptable if they contain the available incident energy
or required level of PPE.

As many forum visitors know, I have been pretty vocal about the restrictive nature of “either / or� language found in the 2009 edition and even in the proposed 2012 draft that did not make it.

The new language for the 2012 edition gives the ability to list incident energy, arc rating, levels and categories. You do not have to list them all - and it is a good idea not to, but the option is there.

Much better! A huge thank you goes out to the NFPA 70E committee for this one!

So here is this week’s question: (finally :) )

When it comes to the 2012 NFPA 70E requirements for defining PPE, which of the following will you be using on your labels from now on for defining PPE

  • Available incident energy and the corresponding working distance
  • Minimum arc rating of clothing
  • Required level of PPE
  • Highest Hazard/Risk Category (HRC) for the equipment

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 1 post ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883