When establishing an electrically safe work condition, do you also apply grounds to the circuit?
|
|
| Author: | rovinnaki [ Mon Mar 05, 2012 12:14 pm ] |
| Post subject: | |
We don't bother earthing out LV circuits but anything MV and above is not deamed Isolated until earths are applied to the circuit. Dave Sargent Origin Energy NZ |
|
| Author: | gilmomoney [ Fri Mar 16, 2012 10:55 am ] |
| Post subject: | |
i second what Dave said...we'll perfrom voltage checks on the LV side and then ground out the MV systems. |
|
| Author: | Gary B [ Fri Mar 16, 2012 9:22 pm ] |
| Post subject: | |
Has much to do with context. Some facilities are more comfortable with a visible open; i.e: withdraw the breaker; but on systems with overhead distribution lines (exposure to accidental energization or induced voltage) grounding is the norm, always. |
|