What short circuit source data do you use for the arc flash study?
Whatever the utility provides 65%  65%  [ 17 ]
Maximum/infinite bus 0%  0%  [ 0 ]
Minimum/contingency case 0%  0%  [ 0 ]
Maximum and minimum 27%  27%  [ 7 ]
Something else 8%  8%  [ 2 ]
Total votes : 26
Author Message
 Post subject: Electric Utility Company Short Circuit Data
PostPosted: Sun Mar 18, 2012 11:24 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
There has been quite a bit of discussion lately about utility short circuit data used in arc flash studies. There are many options such as using the data from the utility company without question, using a minimum value that may represent a a contingency such as a line or transformer out of service, using a maximum short circuit current from an infinite bus, or something else.

This week's question:

What short circuit source data do you use for the arc flash study?

  • Whatever the utility provides
  • Maximum/infinite bus
  • Minimum/contingency case
  • Maximum and minimum
  • Something else

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Mar 18, 2012 1:44 pm 

Joined: Fri Mar 16, 2012 7:14 pm
Posts: 7
I use the utility value so far. If not available, there is a good paper from Eaton, attached.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Mar 19, 2012 1:52 pm 

Joined: Tue Mar 02, 2010 1:50 pm
Posts: 26
Since I am in the utility I often get fault data at the substation, then model the distribution circuit. I usually will use plus or minus 10% for the scenarios and vary the line impedance by 10%.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Mar 19, 2012 5:21 pm 

Joined: Wed Oct 20, 2010 11:46 am
Posts: 12
It can take quite a while for us to model a system, depending on the number of projects we have going on, utility response, etc.
So, for starters we use an infinite bus, or utility data if available, for short circuit duty rating and submittal approval.
then, by the time the equipment is installed and the settings are ready, hopefully we have our Arcflash studies complete. That's the plan anyway. We've gotten bit on a few jobs needing to replace OCPDs to change the curves enough to lower the values to a more workable level.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883