Where lights are controlled from a lighting panel, what protection is used to operate the breaker?
Nothing Special
Clothing and protection based on Table H.3(B)
Something else - we would love to hear the stories
We don't use breakers to control lights
You may select 1 option

View results
Author Message
 Post subject: PPE Used for Operating Lighting Circuit Breakers
PostPosted: Sun Aug 12, 2012 9:35 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1635
Location: Scottsdale, Arizona
This week’s question might “spark” a bit of debate.

If one uses the Hazard / Risk Tables in NFPA 70E, the task of turning the lights on at the office in the morning is classified as HRC 0. This is true of both 120V and 277V breakers. Calculations could lead to the same result i.e. incident energy < 1.2 calories/cm^2.

According to Table H.3(b), HRC 0 requires non-melting fabric/untreated natural fiber, hearing protection, long sleeve shirt etc.

This week’s question:

Where lights are controlled from breakers at a lighting panel, what protection do employees/staff use to turn on the lights?
  • Nothing special
  • Clothing and Protection based on Table H.3(b)
  • Something else - we would love to hear the stories
  • We don't use breakers to control lights

_________________
Jim Phillips, P.E.
Brainfiller.com


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Aug 13, 2012 7:36 am 
Sparks Level

Joined: Wed Oct 29, 2008 6:06 am
Posts: 136
Location: Michigan
[font=Tahoma]The 2012 70E Handbook actually gives this example towards end of annex F to illustrate the process of performing a hazard assessment and risk analysis.[/font]


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Aug 14, 2012 7:48 am 

Joined: Fri Sep 05, 2008 8:10 am
Posts: 36
Initially had nothing special, just quick training on proper operation; stand off to the side, turn head, etc. But we always questioned the need for CAT 0. Then a 30 year old breaker failed an flashed at a woman, no injuries, she was just scared. We had proceeded to install switching outside of the panel to eliminate the need for the breakers used as switches.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Aug 20, 2012 3:59 pm 
Sparks Level
User avatar

Joined: Sat Jun 07, 2008 5:11 pm
Posts: 143
Location: Connecticut
Just because it looks similar to a switch it's not... it's designed to be a protection device. This is a case of the wrong device for the wrong application... unless the breaker is switch duty rated. Or more likely the company is too cheap to spend $15 worth of materials for a dedicated UL listed "on-off" switch.


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Aug 23, 2012 8:09 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Speaking of 120V arc flash, any updates on the IEEE research on the <240V <125kVA issue?


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Aug 26, 2012 2:22 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1635
Location: Scottsdale, Arizona
Zog wrote:
Speaking of 120V arc flash, any updates on the IEEE research on the <240V <125kVA issue?

Nothing new, it's stuck in the ditch of substantial debate for now. We meet again this autumn and there will probably be many new things to report at that time. Stay tuned!

_________________
Jim Phillips, P.E.
Brainfiller.com


Report this post
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Sep 24, 2012 7:02 pm 
Sparks Level

Joined: Thu Oct 18, 2007 7:10 pm
Posts: 263
Location: NW USA
I hope you are able to bring common sense to these committees, because this is where standards committees loose much credibility. Many churches were wired without light switches depending instead on a switching duty panel installed at the rear. One cannot imagine the bell ringer donning arc Flash PPE to turn on the lights. Keep it real folks.

I'm sure we can find extreme cases where this didn't work well, however; building a code around extreme cases is not necessarily improving safety.


Report this post
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


You can post new topics in this forum
You can reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883